I checked with a colleague, and she suggested Moisture Detection Imaging (MDI) as a way to check the condition of the insulation. Moisture in the insulation means corroded pipes, while dry insulation means there is a lower risk. You are correct, thermal images of aluminum sheathing are basically just reflections and you can't trust them.
The rest of her response:
Possible options depending on the pipe design and diameter can be found in API 583 Recommended practice, it has information of advantages and disadvantage:
- Guided Wave
- It is an ultrasonic test
- It requires removal to place the transducer and it is limited to the flange to flange distance, since the signal will not pass those points.
- It can detect inside an outside metal loss
- Radiography
- For pipe < 8in
- Do not detect external chloride stress corrosion cracking on austenitic and duplex materials
- Not removal of insulation required
- Recommended to specific areas suspected to have CUI
- Different technologies available
- Film profile radiography
- Computed and digital detector array (DDA) profile radiography
- Linear diode array
- Film density radiography complementary to profile radiography
- Flash radiography
- Radiometric profiling
- Real time radiography examination method (RTR)
- Pulse Eddy current (PEC) We have used this method on Glycol vessels
- Detect average wall loss outside and inside
- No removal of insulation
- Electromagnetic examination
- Neutron Backscatter
- Moisture detection\
- No removal of insulation
- Thermal imaging (thermography)
- Detection of wet spots in the insulation
- No removal of insulation
- Moisture Detection Imaging (MDI)
- Detect fluids on insulation (organic compounds detection)
- No removal of insulation
------------------------------
Dale Nicholson, PE, CMRP, CRL
Reliability Engineer
Evonik Corp
Lafayette IN
------------------------------
Original Message:
Sent: 06-14-2022 04:17 PM
From: patrick girard
Subject: Inspection isolate bunker line
H everyone,
i have some issues about inspection of a 45 years old line of bunker.
i only have 1 line.
i know it was corrode and i dont want to remove all isolate to inspect.
My staff done thermographic inspection but with the reflectibility of the aluminium coating over isolation, i'm spectical of the result
any feedback about how can i do that to by effective and in operation?
thanks
Patrick
------------------------------
patrick girard
maintenance manager Port and Handling
Arcelormittal
Port-Cartier QC
------------------------------