Randy
I assume you are looking at harmonics if you are discussing filters per device. There are a few options including an active harmonic filter, which would be located at your supply and it basically injects voltage/current harmonic signals 180 degrees from the harmonics in the facility. These have come down in cost significantly but, at 100 Amps or less, may be more expensive than at the equipment itself. Companies like Danfoss produce them. You can also look at, as you mention, straight filters at each instrument in which you would need to determine sizing and type (capacitive - voltage, inductive - current, or both). Finally, in both cases, check your grounds and neutrals to see if harmonic mitigation is needed there, as well, such as with Onics Energy Solutions.
Basically, it depends on your application and the number of devices involved.
Howard W Penrose, Ph.D., CMRP
MotorDoc LLC
Lombard, Illinois
Sent: 03-30-2023 02:07 PM
Subject: Power Conditioning
I'm looking for the best practices for conditioning power to our lab that uses100 amp or less. Should we install filters for each instrument. We recently lost an old conditioner that can't be repaired.
Randy Rhodes
Curia
Hutchinson KS