I checked with a colleague, and she suggested Moisture Detection Imaging (MDI) as a way to check the condition of the insulation. Moisture in the insulation means corroded pipes, while dry insulation means there is a lower risk. You are correct, thermal images of aluminum sheathing are basically just reflections and you can't trust them.
The rest of her response:
Possible options depending on the pipe design and diameter can be found in API 583 Recommended practice, it has information of advantages and disadvantage:
- Guided Wave
- It is an ultrasonic test
- It requires removal to place the transducer and it is limited to the flange to flange distance, since the signal will not pass those points.
- It can detect inside an outside metal loss
- Radiography
- For pipe < 8in
- Do not detect external chloride stress corrosion cracking on austenitic and duplex materials
- Not removal of insulation required
- Recommended to specific areas suspected to have CUI
- Different technologies available
- Film profile radiography
- Computed and digital detector array (DDA) profile radiography
- Linear diode array
- Film density radiography complementary to profile radiography
- Flash radiography
- Radiometric profiling
- Real time radiography examination method (RTR)
- Pulse Eddy current (PEC) We have used this method on Glycol vessels
- Detect average wall loss outside and inside
- No removal of insulation
- Electromagnetic examination
- Neutron Backscatter
- Moisture detection\
- Thermal imaging (thermography)
- Detection of wet spots in the insulation
- Moisture Detection Imaging (MDI)
- Detect fluids on insulation (organic compounds detection)
Lafayette IN