You may already have the ability, depending on your switchgear relay system. This might be a GE Multilin, SEL, Siemens, or other device that is displaying voltage, current, etc. The Device Number is 27 (undervoltage relay) and most of these monitoring systems can be used to trigger or trip the main or individual circuit breakers to bring your system offline or trigger the startup of an alternate source (generator, UPS, etc.).
If you are looking at individual systems such as an AC system (from your title) smaller relay devices are available for motors, MCC, or individual systems.
Howard
------------------------------
Howard W Penrose, Ph.D., CMRP
Random Past SMRP Chair (2018), 2019+ Govt Relations Smart Grid, Infrastructure and Cybersecurity Working Group Chair,
Chair Technical Standards wind, solar, energy storage, American Clean Power (formerly AWEA), and
President
MotorDoc LLC
Lombard, Illinois
------------------------------